        A few months back I moved my laundry room from a cramped closet to a different area of my house. There was not a hot water line running to this room but there is an exterior outside faucet on the wall we relocated our washing machine to. The plumber tapped into that outside exterior wall faucet and installed a new water heater off of that line. This water heater only services the laundry room's washing machine. Over the holidays I noticed that the cold side line of the water heater was warm (actually rather hot) to the touch. I texted my plumber to see if i needed a check valve or something, and his reply was:
        "It's called thermo expansion and you only need it if you had a closed system and your system is not closed."

        This doesn't make any sense to me. I can't see how this is efficient or normal. Is this really nothing to worry about? Or, is my plumber incorrect? When I shutoff the water to the house using my inside shutoff (pre-water filter), that outside faucet also is off. Hence, the exterior faucet is part of my house copper lines and not on it's own system.

        This message has been edited. Last edited by: Xfratboy,
         
        Posts: 1 | Registered: Jan 07, 2013Reply With QuoteReport This Post
        Picture of CommonwealthSparky
        posted Hide Post
        Nipples are available that have plastic check valves installed that tend to help hold the "hot" where it belongs. [In the tank]. 3/4" in diameter,about 2" long, one for the cold, one for the hot, they are threaded into the unit before you would do the rest of the hock up.
        Might they be missing? This could be the problem. If so a trip to your local hardware store, a pipe wrench and teflon paste is a rather strait forward fix. {I'm old school, I would rather use paste than tape.} But that is just me.
        And yes you are heating standing water so you do have an energy & money waste present.


        "Why isn't everyday Earth Day ?"
         
        Posts: 948 | Location: Central Pennsylvania | Registered: Jun 02, 2010Reply With QuoteReport This Post
        posted Hide Post
        I installed a set of those in the folks' house when I replumbed it to copper. hot water flow was restricted, and a couple years later, I pulled 'em out. brown with what I assume was organic material.

        the pipes didn't grow any of that stuff.

        it's a catch-22, those check valves. yeah, they isolate hot from cold. but that is considered a backup safety device as hot water expands slightly.

        I'm not doing them again.


        sig: if this is a new economy, how come they still want my old-fashioned money?
         
        Posts: 4817 | Location: North Burbs, MN | Registered: Mar 14, 2007Reply With QuoteReport This Post
        posted Hide Post
        Wouldn't you need to install an expansion tank if you put a check valve on the water line? A water heater will push the expanding water back towards the meter as the water heats. It isn't much, but it does need a place to go.


        General Disclaimer

        Any advice given here is general in nature and is not necessarily valid for your given area. If in doubt check with your local codes enforcement department for what is required when doing electrical, plumbing or structural work on your house. Permits may or may not be required in your area and home owners may not be able to DIY some tasks. I have no way of knowing if you have the skills needed to complete the tasks you are asking about, when in doubt seek professional assistance.

        My advice may be worth exactly what you pay me for it. :-) For the record I did not stay in a Holiday Inn Express last night.
         
        Posts: 241 | Location: Cary, NC | Registered: Aug 17, 2006Reply With QuoteReport This Post
        Picture of Frodo
        posted Hide Post
        its not hurting a thing. worry only if you start getting hot water coming out of a fixture
        sence you are not useing the fixture often, the water in tank is heating up and expanding. it wont hurt a thing
        if it does get to bothering you have your plumber install an expansion tank
        or a expansion loop in the piping system
         
        Posts: 3370 | Location: I live in southern mississippi | Registered: Jun 01, 2008Reply With QuoteReport This Post
        posted Hide Post
        My town will be adding check valves at the water meters, when they do we need to have an expansion tank installed. Not sure where you think the water is going to expand to while heating. The only place it has to go is out the TPV if a check valve prevents it from going back out the cold water line towards the main.

        When I replaced my water heater a few years ago I added an expansion tank.


        General Disclaimer

        Any advice given here is general in nature and is not necessarily valid for your given area. If in doubt check with your local codes enforcement department for what is required when doing electrical, plumbing or structural work on your house. Permits may or may not be required in your area and home owners may not be able to DIY some tasks. I have no way of knowing if you have the skills needed to complete the tasks you are asking about, when in doubt seek professional assistance.

        My advice may be worth exactly what you pay me for it. :-) For the record I did not stay in a Holiday Inn Express last night.
         
        Posts: 241 | Location: Cary, NC | Registered: Aug 17, 2006Reply With QuoteReport This Post
        Picture of CommonwealthSparky
        posted Hide Post
        I too have scene houses in these parts that have expansion tanks tied into the water heater. But only a few, compared to all the oil or coal boilers. Certainly would make sense, expansion wise. Wink


        "Why isn't everyday Earth Day ?"
         
        Posts: 948 | Location: Central Pennsylvania | Registered: Jun 02, 2010Reply With QuoteReport This Post
        Picture of Frodo
        posted Hide Post
        yes it does. but you can do it cheaper
        by using an expansion loop
        run a straight line of pipe, north to south, make a 90 degree offset east 12 inch
        then a 90 degree offset north. 5 ft
        90 degree west 12 inch
        then reconnect to the north/south straight line
        simple, expansion loop
        we use it to expand steam lines and hot water heating lines
         
        Posts: 3370 | Location: I live in southern mississippi | Registered: Jun 01, 2008Reply With QuoteReport This Post
        posted Hide Post
        quote:
        Originally posted by CommonwealthSparky:
        I too have scene houses in these parts that have expansion tanks tied into the water heater. But only a few, compared to all the oil or coal boilers. Certainly would make sense, expansion wise. Wink


        They only started requiring them when the looked to add check valves to protect the public water supply from possible contaminants getting pulled into the system in case of a water main break. If for example you had a hose end yard chemical sprayer attached to a hose in the event of a break the vacuum could pull this into the public water supply. It is my understanding that is why the toilet fill valves have the little hose that dumps water down the overflow while filling. If there was a break the pressure would suck air and not tank water.

        Anyway, the tanks run less the $40. I'm not a plumber but I think Frodo's solution is to compensate for the expansion of the pipes as they get heated by the water. They do the same thing on oil pipelines to compensate for the expansion from the hot oil.


        General Disclaimer

        Any advice given here is general in nature and is not necessarily valid for your given area. If in doubt check with your local codes enforcement department for what is required when doing electrical, plumbing or structural work on your house. Permits may or may not be required in your area and home owners may not be able to DIY some tasks. I have no way of knowing if you have the skills needed to complete the tasks you are asking about, when in doubt seek professional assistance.

        My advice may be worth exactly what you pay me for it. :-) For the record I did not stay in a Holiday Inn Express last night.
         
        Posts: 241 | Location: Cary, NC | Registered: Aug 17, 2006Reply With QuoteReport This Post
          Powered by Social Strata  
         

            DIY Message Boards  Hop To Forum Categories  Home Improvement  Hop To Forums  Plumbing    Cold water inlet to water heater is hot to touch

        © Scripps Networks 2009

        Advertisement

        Posting Guidelines

        • Please be sure posts are category appropriate.
        • No off-topic or off-color postings.
        • Postings may be deleted at the discretion of DIY moderators.
        • No advertising is allowed.
        • Be nice. No name calling, personal attacks or flaming.
        • Certain words will trigger moderation of the post. These words mostly cover political or religious topics, which are OFF the topics covered by DIY.

        Full Guidelines

        For general message board help, click the tab labeled "Tools," and choose "Help" from the dropdown menu.