        Allowable horizontal run to vent/drain Sign In/Join 
        posted
        Greetings all,

        I suppose I could find this in the code if I looked long enough, but hopefully this is simple enough. I am moving a pair of sinks horizontally along a wall 2 to 3 feet from the existing drain/vents. I want to Tee into the existing drain/vent and install a horizontal run to the new stub-out. How far can I run horizontally from the drain/vent to the new stub-out?


        Do Well.
         
        Posts: 13 | Registered: Jan 03, 2014Reply With QuoteReport This Post
        Picture of Jaybee
        posted Hide Post
        There is no true horizontal drain run - all need to have at least 1/4" per foot pitch.

        At that pitch, you can run any distance but your vent tie-in needs to be within 5' of the sink.

        This message has been edited. Last edited by: Jaybee,


        Jaybee
         
        Posts: 10430 | Location: Knoxville, Tennessee | Registered: Sep 27, 2003Reply With QuoteReport This Post
        posted Hide Post
        Five feet....Thanks!


        Do Well.
         
        Posts: 13 | Registered: Jan 03, 2014Reply With QuoteReport This Post
        Picture of Frodo
        posted Hide Post
        5' on a 2" drain horizontial line
        3' on a 1 1/2" drain line
        what are you tieing into? is it a waste stack? that has no other drains on it? or is it a line with other lines tied into it?
         
        Posts: 4062 | Location: I live in southern mississippi | Registered: Jun 01, 2008Reply With QuoteReport This Post
          Powered by Social Strata  
         

            DIY Message Boards  Hop To Forum Categories  Home Improvement  Hop To Forums  Plumbing    Allowable horizontal run to vent/drain

        © Scripps Networks 2009

        Advertisement

        Posting Guidelines

        • Please be sure posts are category appropriate.
        • No off-topic or off-color postings.
        • Postings may be deleted at the discretion of DIY moderators.
        • No advertising is allowed.
        • Be nice. No name calling, personal attacks or flaming.
        • Certain words will trigger moderation of the post. These words mostly cover political or religious topics, which are OFF the topics covered by DIY.

        Full Guidelines

        For general message board help, click the tab labeled "Tools," and choose "Help" from the dropdown menu.