Allowable horizontal run to vent/drain

This topic can be found at:
http://boards.diynetwork.com/eve/forums/a/tpc/f/2791013504/m/2193963008

Jan 11, 2014, 12:11 PM
todd1956
Allowable horizontal run to vent/drain
Greetings all,

I suppose I could find this in the code if I looked long enough, but hopefully this is simple enough. I am moving a pair of sinks horizontally along a wall 2 to 3 feet from the existing drain/vents. I want to Tee into the existing drain/vent and install a horizontal run to the new stub-out. How far can I run horizontally from the drain/vent to the new stub-out?


Do Well.
Jan 11, 2014, 04:26 PM
Jaybee
There is no true horizontal drain run - all need to have at least 1/4" per foot pitch.

At that pitch, you can run any distance but your vent tie-in needs to be within 5' of the sink.

This message has been edited. Last edited by: Jaybee,


Jaybee
Jan 11, 2014, 10:49 PM
todd1956
Five feet....Thanks!


Do Well.
Jan 15, 2014, 07:50 PM
Frodo
5' on a 2" drain horizontial line
3' on a 1 1/2" drain line
what are you tieing into? is it a waste stack? that has no other drains on it? or is it a line with other lines tied into it?